Post 1 made on Thursday December 11, 2003 at 20:21
RWI
Founding Member
Joined:
Posts:
December 2001
592
I have 3 Switchlinc 2386 switch's in a 3 gang box. 2 are running 4) 120W bulbs, and the other is running 3) 120W bulbs. All works o.k. however the switch's are getting hotter than I am comfortable with. I remember reading some where about replacing the plastic 3gang box to a metal type as it would act as a heatsink. Also I think that it said something about removing close by insulation. What are your thoughts and suggestions. Thanks!
Post 2 made on Friday December 12, 2003 at 00:55
AutomatedOutlet
Long Time Member
Joined:
Posts:
November 2003
215
Hi,

You're running 480 watts on a 600 watt switch. You're certainly within the specs of the switch but you should expect some heat. Three of those switches will get crowded in there but it's OK. Replacing the switch box sure sounds like a lot of work. If anything, I might consider switching to a 1000 watt switch (although it's not necessary).

Martin
Martin@AutomatedOutlet.com
OP | Post 3 made on Friday December 12, 2003 at 20:56
RWI
Founding Member
Joined:
Posts:
December 2001
592
Well Martin, I can't say that I agree with you,

1. When you install 2 or more of these switch's together the power handling drops by 200 watts. ( I am unclear if you have 3 switch's together whether the center switch drops by 200 or 400 watts.

2. As far as I could find out the only difference with the 1000 watt switch's is a larger triac which will not run any cooler, only last longer

Perhaps Larry Fine can shed some more light on this as he certainly seems to have the most knowledge on these kinds on things.
Post 4 made on Saturday December 13, 2003 at 00:27
Larry Fine
Loyal Member
Joined:
Posts:
August 2001
5,002
Boinggg!!!

The derating usually works like this:

1 unit, 600 watts
2 units, 500 watts
3 or more, 400 watts

So, you are actually exceeding the ratings a tad on two of them. The little-but-useful idea might be to place the 3-fixture unit in the center.

You could always use a steel plate with a thick smear of conductive goop behind it, and maybe drill a few 1/4" holes in the top and bottom of the box. Watch the wires, both inside and outside the box!

Larry
www.fineelectricco.com
OP | Post 5 made on Saturday December 13, 2003 at 11:39
RWI
Founding Member
Joined:
Posts:
December 2001
592
Thanks for the reply Larry,

I took this right out of the switchlinc manual.

Mounts in a single or multiple-ganged j box (200W of load control is lost on 600W switchlinc for each immediately adjacent dimmer installation; 600W Load control becomes 400W with a switchlinc to the immediate right or left

So what does this mean for the center switch in my situation?
Post 6 made on Saturday December 13, 2003 at 11:46
Larry Fine
Loyal Member
Joined:
Posts:
August 2001
5,002
I was thinking that the coolest-running dimmer would be the least harmful, just to keep the others apart. According to the manual, you are overloading two of yours, w/480 watts, while the third is just under, at 360 watts.

Could you live with 90-watt bulbs instead of the 120's? That you use dimmers indicates that you don't need 120 watts per all the time. If all you want is on-off control, non-dimming units could be used.

If you must keep the bulbs you have now, I still think the best compromise is to place the lower-loaded dimmer in the middle postition. The best scenario would be to use three separate boxes.

Larry
www.fineelectricco.com
OP | Post 7 made on Saturday December 13, 2003 at 21:39
RWI
Founding Member
Joined:
Posts:
December 2001
592
Larry,

I do have the 3 bulb circuit in the center position, The room in question is a large finished basement with 10ft ceilings. Yes I could use 90W bulbs but it is a little dim at times. Let me ask you this, if I set the default on value of the switch's to 75% (if I under stand this correctly that would equal 90W) and just use full on say for cleaning and such would that be o.k. If not would you suggest going to the 1000W switch's or perhaps a differant type of bulb (I have tried halogen floods but it gave a much more uneven look) is there some other type of bulb to look at? As I said the basment is already finished so changing to 3 seperate box's would be tough now. Thanks again RWI
OP | Post 8 made on Tuesday December 16, 2003 at 21:47
RWI
Founding Member
Joined:
Posts:
December 2001
592
Any other thoughts Larry?


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.