HMDI Matrix Switch control using RS232
| |
|
Topic: | HMDI Matrix Switch control using RS232 This thread has 8 replies. Displaying all posts. |
|
Post 1 made on Sunday June 21, 2020 at 09:57 |
Pambs Long Time Member |
Joined: Posts: | January 2007 54 |
|
|
I am trying to connect it through RS232. I have used a 3pin phoinix connector and included the commands like the below
RS232 Commands The SY-MUHD-44 and SY-MUHD-88 can also be controlled using RS232 commands, and some configuration settings can only be performed using RS232 commands. The same commands can sent to the matrix via the Ethernet, as IP commands.
The serial port settings should be set to: 57600,n,8,1 (baud: 57600, no parity, 8 data bits and 1 stop bit) with no handshaking.
In each of the following RS232 command the symbol represents the carriage-return character (0x0d). Where shown for a particular command, the square brackets [] are required for that command. The commands normally reply with the same command that was sent, but with the fist character pointing left: e.g. the command: >@WVSO[1]I[2] gives the command response: <@WVSO[1]I[2] Video Selection Commands Change the input and output signal routing: Where x is the input number and y is the output number. >@WVSO[y]I[x] Set input x to all outputs >@WVSOA[x] Turn output y off >@WVSO[y]OFF Turn output y on >@WVSO[y]ON
Do i need to add something more on this code? Because still is not responding. Added it as ASCII
>@WVSO[1]I[2]
Specs link with manual
|
|
Post 2 made on Sunday June 21, 2020 at 12:49 |
Lyndel McGee RC Moderator |
Joined: Posts: | August 2001 12,992 |
|
|
1. Have you used Telnet or Windows Hyperterminal to test this? 2. Where is the prontoscript that you are attempting to use to do this?
You did not paste the link to the protocol spec so everything here you state is hypothetical.
How are your sending the 0x0d? Are you escaping this within your string using '\r'? I would love to help but you have given me nothing other than asking how to build a command for your equipment.
|
Lyndel McGee Philips Pronto Addict/Beta Tester
|
|
OP | Post 3 made on Monday June 22, 2020 at 03:11 |
Pambs Long Time Member |
Joined: Posts: | January 2007 54 |
|
|
Hi Lyndel okay i thought this was simpler to be honest. Maybe it's above my knowledge and need to read more. I just created the component and added the commands based on what i understood. Here are a couple of pictures on how i have set it up [Link: ibb.co][Link: ibb.co]
|
|
Post 4 made on Monday June 22, 2020 at 20:18 |
Lyndel McGee RC Moderator |
Joined: Posts: | August 2001 12,992 |
|
|
The Building Blocks view in the 2nd pic does not show the Matrix Switcher component to verify that you have configured it to use a Serial Port on your RFX9600.
That being said, the problem is most likely in the command you are sending. All your functions end with '?'. Why is that? Because you copy/pasted? You need to replace the '?' at the end of each function with \r which is the escaped ASCII character for Carriage Return (Hexadecimal 0x0d).
Lyndel
|
Lyndel McGee Philips Pronto Addict/Beta Tester
|
|
OP | Post 5 made on Thursday June 25, 2020 at 02:04 |
Pambs Long Time Member |
Joined: Posts: | January 2007 54 |
|
|
Hi Lyndel I had the selection on the MC12 when i took the screenshot. Here is how it's configured. I have updated the commands as well but they are not working [Link: ibb.co][Link: ibb.co]
|
|
Post 6 made on Thursday June 25, 2020 at 17:52 |
Lyndel McGee RC Moderator |
Joined: Posts: | August 2001 12,992 |
|
|
Why is there a yellow 'Yield sign' icon on the activity in question? Could it be that you have not replaced the component from MyDatabase after editing the commands in the database?
If this is indeed the case, replace the component with updated one from MyDatabase or try exporting as a PackAndGo exe file to find out why the warning is there.
If you've done all this, then consider swapping pins 2 and 3 in one end of your serial cable to check whether you need a straight cable or a crossover cable.
|
Lyndel McGee Philips Pronto Addict/Beta Tester
|
|
OP | Post 7 made on Friday June 26, 2020 at 02:43 |
Pambs Long Time Member |
Joined: Posts: | January 2007 54 |
|
|
The yellow sign should be some cosmetic change i did not download when i took the picture. I will try the pins i was also thinking the same
|
|
Post 8 made on Friday June 26, 2020 at 21:33 |
Lyndel McGee RC Moderator |
Joined: Posts: | August 2001 12,992 |
|
|
Try to get it working with same cable using a PC with an RS232 port and hyperterminal.
|
Lyndel McGee Philips Pronto Addict/Beta Tester
|
|
OP | Post 9 made on Thursday July 9, 2020 at 06:49 |
Pambs Long Time Member |
Joined: Posts: | January 2007 54 |
|
|
switched the pins and it worked fine. look like it needed cross cable setup
|
|
|
Before you can reply to a message... |
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now. |
Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.
|
|
|
|